    Program Description:

    "ASCE798W" is a spreadsheet program written in MS-Excel for the purpose of wind loading analysis for buildings
    and structures per the ASCE 7-98 Code. Specifically, wind pressure coefficients and related and required
    parameters are selected or calculated in order to compute the net design wind pressures.

    Worksheet Name Description

    Stacks & Tanks Analysis of cantilevered chimneys, stacks, and vertical tanks
    Wind Map Basic wind speed map (Figure 6-1 of ASCE 7-98 Code)

    Program Assumptions and Limitations:

    1. This program assumes only enclosed or partially enclosed buildings. Open buildings are NOT considered.
    2. Worksheet for Simplified analysis is applicable for buildings meeting the criteria of Section 6.4.1.
    3. In the worksheet for Simplified analysis, the design MWFRS wind load is calculated for each direction.
    This design load is assumed equal to 1/2 of the total load, as 1/2 is assumed to be taken at roof level and
    the other 1/2 is taken at the base of the building.
    4. Worksheet for MWFRS (Low-Rise) is applicable for low-rise buildings as defined in Section 6.2.
    5. Worksheets for MWFRS (Any Ht.), Wall C&C, and Roof C&C are applicable for buildings with mean roof
    heights of up to 500 feet.
    6. Worksheet for Stacks & Tanks is applicable for cantilevered structures up to 600 feet tall.
    7. Worksheets for Wall C&C and Roof C&C are applicable for flat roof buildings, gable roof buildings with roof
    angles <= 45 degrees, and monoslope roof buildings with roof angles <= 3 degrees.
    8. Worksheets for MWFRS (Any Ht.) and for Stacks & Tanks can handle “rigid” as well as “flexible” buildings
    and structures. For “rigid” buildings or structures, this program uses the smaller value of either 0.85 or the
    calculated value from Section 6.5.8.1 of the Code for the gust effect factor, 'G'. For “flexible” buildings or
    structures, this program calculates the gust effect factor, ‘Gf’, per Section 6.5.8 of the Code based on the
    assumed formula for the fundamental period of vibration from Section 9.5.3.3 of the Code.
    9. This program uses the equations listed in the reference, “Guide to the Use of the Wind Load Provisions"

    Online calculator here:

    Wind Loading Building Any Height
    Last edited by Kelly_Bramble; 11-04-2015 at 03:15 PM.

  2. #2
    flippenmh
    Guest
    The download you have attached doesn't seem to work. Do you have another link, or can you email it?

    email removed
    Last edited by Kelly_Bramble; 07-18-2014 at 09:20 AM.

  3. #3
    Technical Fellow Kelly_Bramble's Avatar
    Join Date
    Feb 2011
    Location
    Bold Springs, GA
    Posts
    2,624
    Download verified as fully functional..