Re: BTU removal


[ Home ][ Forum Archive ] [ Active Engineering Forum ]

Posted By<" ">William on October 25, 2002 at 17:37:23:

In Reply to: BTU removal posted byJames Partain on October 23, 2002 at 15:14:30:

: If I have ambient air temperature of 80°F, 80 percent relative humidity and I want to maintain a maximum of 105°F in an enclosure while removing 1783019 BTU's per hour produced by an electric motor, how many CFM's do I need? Enclosure is 3,032 cubic feet ID.

: James Partain

Here's a formula that will give you a rough order of magnitude.

CFM= kW/temp rise x 3000 (a constant)

Using your numbers:
CFM= 522.2kW/25 degree rise x 3000= 62,664 CFM
Assuming zero losses.

A blower capable of this CFM at 2" s.p. would be about 60" dia. Rotating at 550 rpm, with a 40 hp motor.

So say your room is 10'w x 10'h x 30'long, the air flow traveling lengthwise would be 620feet per minute (approx) a wind tunnel almost.

I maintain that your heat load is less than you have stated. Arriving at your actual heat load you will realize your CFM needs will be lower.

Good Luck
William