Fire Sprinkler Discharge Calculator (simplified)
This calculator determines the typical discharge vs flow rate of a sprinkler head
Preview: Fire Sprinkler Discharge Calculations
Eq.1
Q = n · [ K · P1/2 ]
Where
Q = flow (gpm)
K = measure of the ease of getting water out of the orifice, related to size and shape of the orifice in units of gpm per (psi)1/2
P = pressure (psi)
n = number of sprinkler heads (identical at same pressure)
Sprinkler K Factors (typical)
Orifice Size |
Name |
K Factor |
1/2" |
Standard |
5.6 |
17/32" |
Large |
8.0 |
5/8" |
Estra Large |
11.2 |
NFPA Standard 291, Recommended Practice for Fire Flow Testing and Marking of Hydrants.
- Blowdown Time in Unsteady Gas Flow Calculator and Equation . Blowdown is a planned or unplanned release of pressurized gas from storage or containment.
- Fluids Dynamic Simulator and stress reliever
- Fluid Stream From a Container Distance and Coordinates Equations and Calculator
- Flow Through a Sluice Gate Formula and Calculator
- Flow over Channel Rise Hump Formula
- Fluid Flow Discharge Time under Falling Head Formula and Calculator
- Head Changes Caused by Pipe Size Enlargement Formula and Calculator
- Head Changes Caused by Pipe Size Sudden Reduction Formula and Calculator
- Pitot-Static Tube Velocity of Fluid Flow Measurement Calculator and Equation
- Orifice Submerged in Liquid Discharge Rate Calculator and Equation
- Flow of Water in Pipes Equations and Calculator
- Flow Rate of Steam in Schedule 40 Pipe Tables
- Velocity of Water Due To Head in Feet Table
- Storm Drain Pipe Sizing Formula and Calculator
- Nozzle, Water Flow Table Units in Cubic Feet per Second