Incident Energy Intermediate Equations and Calculator per IEEE 1584-2018
Intermediate Incident Energy (E) Equations and Calculator per IEEE 1584-2018 for E600 , E2700 , E14300 and E ≤600 at Voc = Volts units (J/cm2)
The predicted arc current and incident energy are used in selecting appropriate overcurrent protective devices and personal protective equipment, as well as defining safe working distance.
Preview: Incident Energy (E) Equations and Calculator per IEEE 1584-2018
Equation 1
E600 Incident Energy (E) Calculator
Open E600 Intermediate Incident Energy (E) Calculator (Pop-up Window)
Premium Membership Required
Equation 2
E2700 Incident Energy (E) Calculator
Open E2700 Intermediate Incident Energy (E) Calculator (Pop-up Window)
Equation 3
E 14300 Incident Energy (E) Calculator
Open E 14300 Intermediate Incident Energy (E) Calculator (Pop-up Window)
Equation 4
E ≤600 Incident Energy (E) Calculator
Open E ≤600 Intermediate Incident Energy (E) Calculator (Pop-up Window)
E600 = incident energy at Voc = 600 V (J/cm2)
E2700 = Incident energy at Voc = 2700 V (J/cm2)
E14300 = Iincident energy at Voc = 14 300 V (J/cm2)
E ≤600 = Incident energy for Voc ≤ 600 V (J/cm2)
G = Gap between electrodes (mm)
Iarc_600 = rms arcing current for 600 V (kA)
Iarc_2700 = rms arcing current for 2,700 V (kA)
Iarc_14300 = rms arcing current for 14,300 V (kA)
I = rms arcing current for Voc ≤ 600 V [obtained using Equation (25)] (kA)
Ibf = Bolted fault current for three-phase faults (symmetrical rms) (kA)
D = Distance between electrodes and calorimeters (working distance) (mm)
CF = Correction factor for enclosure size (CF = 1 for VOA and HOA configurations)
T = Arc duration (ms)
lg = log10
k1 to k13 from table given below
Table A Coefficients (E600 and E ≤600 )
600 V
k1
k2
k3
k4
k5
k6
k7
k8
k9
k10
k11
k12
k13
VCB
0.753364
0.566
1.752636
0
0
-4.783E-09
0.000001962
-0.000229
0.003141
1.092
0
-1.598
0.957
VCBB
3.068459
0.26
-0.098107
0
0
-5.767E-09
0.000002524
-0.00034
0.01187
1.013
-0.06
-1.809
1.19
HCB
4.073745
0.344
-0.370259
0
0
-5.382E-09
0.000002316
-0.000302
0.0091
0.9725
0
-2.03
1.036
VOA
0.679294
0.746
1.222636
0
0
-4.783E-09
0.000001962
-0.000229
0.003141
1.092
0
-1.598
0.997
HOA
3.470417
0.465
-0.261863
0
0
-3.895E-09
0.000001641
-0.000197
0.002615
1.1
0
-1.99
1.04
Table B Coefficients E 2700
2700 V
k1
k2
k3
k4
k5
k6
k7
k8
k9
k10
k11
k12
k13
VCB
2.40021
0.165
0.354202
-1.557E-12
4.556E-10
-4.186E-08
8.346E-07
5.482E-05
-0.003191
0.9729
0
-1.569
0.9778
VCBB
3.870592
0.185
-0.736618
0
-9.204E-11
2.901E-08
-3.262E-06
0.0001569
-0.004003
0.9825
0
-1.742
1.09
HCB
3.486391
0.177
-0.193101
0
0
4.859E-10
-1.814E-07
-9.128E-06
-0.0007
0.9881
0.027
-1.723
1.055
VOA
3.880724
0.105
-1.906033
-1.557E-12
4.556E-10
-4.186E-08
8.346E-07
5.482E-05
-0.003191
0.9729
0
-1.515
1.115
HOA
3.616266
0.149
-0.761561
0
0
7.859E-10
-1.914E-07
-9.128E-06
-0.0007
0.9981
0
-1.639
1.078
Table C Coefficients E 14300
14300 V
k1
k2
k3
k4
k5
k6
k7
k8
k9
k10
k11
k12
k13
VCB
3.825917
0.11
-0.999749
-1.557E-12
4.556E-10
-4.186E-08
8.346E-07
5.482E-05
-0.003191
0.9729
0
-1.568
0.99
VCBB
3.644309
0.215
-0.585522
0
-9.204E-11
2.901E-08
-3.262E-06
0.0001569
-0.004003
0.9825
0
-1.677
1.06
HCB
3.044516
0.125
0.245106
0
-5.043E-11
2.233E-08
-3.046E-06
0.000116
-0.001145
0.9839
0
-1.655
1.084
VOA
3.405454
0.12
-0.93245
-1.557E-12
4.556E-10
-4.186E-08
8.346E-07
5.482E-05
-0.003191
0.9729
0
-1.534
0.979
HOA
2.04049
0.177
1.005092
0
0
7.859E-10
-1.914E-07
-9.128E-06
-0.0007
0.9981
-0.05
-1.633
1.151
VCB: Vertical conductors/electrodes inside a metal box/enclosure
VCBB: Vertical conductors/electrodes terminated in an insulating barrier inside a metal box/enclosure
HCB: Horizontal conductors/electrodes inside a metal box/enclosure
VOA: Vertical conductors/electrodes in open air
HOA: Horizontal conductors/electrodes in open air
IEEE 1584-2018