Minimum Pipe Insulation Thickness per. ASHRAE Table, Formula and Calculator
Heat Transfer Knowledge and Engineering
HVAC Engineering
Minimum Pipe Insulation Thickness, in. per. ASHRAE Table, Formula and Calculator
This table defines the recommended minimum pipe insulation thickness based on the fluid design operating temperature range. The calculator located on the bottom of this webpage will determine an alternate insulation thickness outside of the stated conductivity range.
Economics can be used to (1) select the optimum insulation thickness for a specific insulation, or (2) evaluate two or more insulation materials for least cost for a given level of thermal performance. In either case, economic considerations determine the most cost-effective solution for insulating over a specific period. Life-cycle costing considers the initial cost of the insulation system plus the ongoing value of energy savings over the expected service lifetime. The economic thickness is defined as the thickness that minimizes the total life-cycle cost.
Fluid Design Operating Temp. Range, °F |
Insulation Conductivity |
Nominal Pipe or Tube Size, in. |
Conductivity,
Btu·in/h·ft2·°F |
Mean Rating
Temp., °F |
< 1
1 to < 1 - 1/2
1- 1/2 to < 4
4 to < 8
≥ 8
> 350
0.32 to 0.34 |
250 |
4.5 |
5.0 |
5.0 |
5.0 |
5.0 |
250 to 350
0.29 to 0.32 |
200 |
3.5 |
4.0 |
4.5 |
4.5 |
4.5 |
201 to 250
0.27 to 0.30 |
150 |
2.5 |
2.5 |
3.0 |
3.0 |
3.0 |
141 to 200
0.25 to 0.29 |
125 |
1.5 |
1.5 |
2.0 |
2.0 |
2.0 |
105 to 140
0.22 to 0.28 |
100 |
1.0 |
1.0 |
1.5 |
1.5 |
1.5 |
Cooling Systems (Chilled Water, Brine, and Refrigerant)d |
40 to 60 |
0.22 to 0.28 |
75 |
0.5 |
0.5 |
1.0 |
1.0 |
1.0 |
<40 |
0.22 to 0.28 |
50 |
0.5 |
1.0 |
1.0 |
1.0 |
1.5 |
a For insulation outside stated conductivity range, determine minimum thickness T as follows:
T = r { ( 1 + t / r )K/k - 1 }
t = insulation thickness listed in this table for applicable fluid temperature and pipe
size,
K = conductivity of alternative material at mean rating temperature indicated for
applicable fluid temperature (Btu·in/h·ft2·°F);
k = upper value of conductivity range listed in this table for the applicable fluid temperature.
b These thicknesses are based on energy efficiency considerations only. Additional
insulation is sometimes required relative to safety issues/surface temperature.
c Piping insulation is not required between control valve and coil on run-outs
when control valve is located within 4 ft of coil and pipe size is 1 in. or less.
d These thicknesses are based on energy efficiency considerations only. Issues
such as water vapor permeability or surface condensation sometimes require vapor retarders or additional insulation.
- Minimum Duct Insulation R-Value
- Insulation Material Thermal Conductivity Chart
- Insulation Blanket Applications and Capabilities Overview
- Time to Freeze Piping Formulas and Calculator
- Insulating Materials Thermal Properties
- Heat Loss Insulated Pipe Equation and Calculator
- Heat Loss Insulated Electric Wire Equations and Calculator
- Insulation Resistance for Electrical Equipment Calculator Spreadsheet
- ASME Code for Pressure Piping, B31.5, Refrigeration Piping and Heat Transfer Components