HVAC Air Change Out Frequency (minutes)
Minimum Ventilation Air Exchange Rates in Breathing Zone per. ANSI / ASHRAE Standard 62.1
Per. ANSI / ASHRAE Standard 62.1 - Breathing Zone Outdoor Airflow. The outdoor airflow required in the breathing zone (Vbz) of
the occupiable space or spaces in a ventilation zone shall be not less than the value determined in accordance
withThe following are general recommendations for total volume of air change out for selected type indoor air spaces.
Outdoor Airflow Required in Breathing Zone Calculator
Outdoor airflow required in the breathing zone calculator
Vbz = Rp Pz + Ra Az
Where
Az = zone floor area, the net occupiable floor area of the ventilation zone, ft2 (m2)
Pz = zone population, the number of people in the ventilation zone during use
Rp = See table calculator
Ra = See table calculator
General Ventilation Rates (no references)
HVAC Space Definition |
Air Change Out Frequency (minutes) |
Assembly Halls |
3-10 |
Auditoriums |
4-15 |
Bakeries |
1-3 |
Boiler Rooms |
2-4 |
Bowling Alleys |
2-8 |
Dry Cleaners |
1-5 |
Engine Rooms |
1-1.5 |
Factories (General) |
1-5 |
Forges |
1-2 |
Foundries |
1-4 |
Garages |
2-10 |
Generating Rooms |
2-5 |
Glass Plants |
1-2 |
Gymnasiums |
2-10 |
Heat Treat Rooms |
0.5-1 |
Kitchens |
1-3 |
Laundries |
2-5 |
Locker Rooms |
2-5 |
Machine Shops |
3-5 |
Mills (Paper) |
2-3 |
Mills (Textile) |
5-15 |
Packing Houses |
2-15 |
Recreation Rooms |
2-8 |
Residences |
2-5 |
Restaurants |
5-10 |
Retail Stores |
3-10 |
Shops (General) |
3-10 |
Theaters |
3-8 |
Toilets |
2-5 |
Transformer Rooms |
1-5 |
Turbine Rooms |
2-6 |
Warehouses |
2-10 |
Source ANSI / ASHRAE Standard 62.1 - Breathing Zone Outdoor Airflow
- Accurate Heating and Cooling Load Calculations - Premium Membership Required
- Air Conditioning Size Calculator and Estimator Chart This calculator is provided for use to calculate basic size in BTU to adequately cool a room of know size.
- Air Conditioning System Design and Analysis Document This is an introduction to air conditioning systems (frequently referred to as HVAC systems – heating, ventilating and air conditioning systems).
- Air Flow Through Opening Caused by Wind Only Calculator
- Changeover (Balance) HVAC Temperature Calculator
- Convert Flat Oval Ducts to Round Sizes, Formula and Calculator
- Convert Rectangular or Square Ducts to Round Sizes, Formula and Calculator
- Duct Design Air Flow Velocities - Typical Duct sizes to achieve air flow requirements typical
- Relative Humidity and Weight per Cubic Foot Volume of Air
- Residential Duct Systems Design Calculations Excel Spreadsheet , ACCA Manual D, 3rd Edition
- Humidification Humidifier Load Calculations and Calculator