Fourier's Law for Insulation Formula
HVAC Design and Engineering
Heat Transfer
Alternative resource for calculating heat loss or gain: Heat Loss from Ducts Equations and Calculator
Steady state, one-dimensional heat flow through insulation systems is governed by Fourier’s law:
Fourier's Law Equation
Q = –kA dT/dx
Q = rate of heat flow, Btu/h
A = cross-sectional area normal to heat flow, ft2
k = thermal conductivity of insulation material, Btu/h·ft·°F
dT/dx = temperature gradient, °F/ft
For flat geometry of finite thickness, the equation reduces to:
Q = kA(T1 – T2)/L
where L is insulation thickness, in ft.
For radial geometry, the equation becomes
Q = kA2(T1– T2)/[r2 ln(r2/r1)]
Where
r2 = outer radius, ft
r1 = inner radius, ft
A2 = area of outer surface, ft2
The term r2 ln( r2/r1 ) is sometimes called the equivalent thickness of the insulation layer. Equivalent thickness is the thickness of insulation that, if installed on a flat surface, would equal the heat flux at the outer surface of the cylindrical geometry.
Heat transfer from surfaces is a combination of convection and radiation. Usually, these modes are assumed to be additive, and therefore a combined surface coefficient can be used to estimate the heat flow to and from a surface:
hs = hc + hr
where
hs = combined surface coefficient, Btu/h·ft2·°F
hc = convection coefficient, Btu/h·ft2·°F
hr = radiation coefficient, Btu/h·ft2·°F
Assuming the radiant environment is equal to the ambient air temperature, the heat loss/gain at a surface can be calculated as
Q = hsA(Tsurf – Tamb)
The radiation coefficient is usually estimated as:
hr = ε σ ( T4surp - T4amb) / ( Tsurp - Tamb)
ε = surface emittance
σ = Stephen-Boltzmann constant, 0.1712 × 10-8 Btu/h·ft2·°R4
- Emittance Data of Commonly Used Materials
- Emissivity of Surface Table
- Heat Loss from Ducts Equations and Calculator
- HVAC Air Duct Flow Resistance Chart
- Spiral Duct Machine Review
- Duct Design Air Flow Velocities
- Thermal Linear Expansion of AISI 303 Stainless Steel
- Pipe Expansion Thermal Loop Equations and Calculator
- Coefficients Linear Thermal Expansion
- Compression Tension Stress Linear Thermal Expansion Equation and Calculator
- Linear Thermal Expansion Equation and Calculator
- Thermal Properties of Metals, Conductivity, Thermal Expansion, Specific Heat
- ASHRAE Fundamental Handbook, 2019