Minimum Ventilation Rates in Rooms
Minimum Ventilation Rates in the Breathing Zone, Based on ANSI/ASHRAE Standard 62.1-2007
Occupancy |
Human Outdoor
Air Rate, R cfm/person |
Area Outdoor
Air Rate, Ra cfm/ft2 |
Occupant Density
(see Note 4) #/1,000 ft2 |
Combined Outdoor
Air Rate cfm/person |
Air Class
Educational Facilities | |||||
Daycare (through age 4) |
10
0.18
25
17
2
Classrooms (ages 5–8) |
10
0.12
25
15
1
Classrooms (ages 9 plus) |
10
0.12
35
13
1
Lecture classroom |
7.5
0.06
65
8
1
Art classroom |
10
0.18
20
19
2
Science laboratories |
10
0.18
25
17
2
University/college laboratories |
10
0.18
25
17
2
Wood/metal shop |
10
0.18
20
19
2
Multi-use assembly |
7.5
0.06
100
8
1
Office Buildings | |||||
Office space |
5
0.06
5
17
1
Reception areas |
5
0.06
30
7
1
Main entry lobbies |
5
0.06
10
11
1
Miscellaneous Spaces | |||||
Electrical equipment rooms |
0.06
1
Shipping/receiving |
0.12
1
Warehouses |
0.06
2
Public Assembly Spaces | |||||
Auditorium seating area |
5
0.06
150
5
1
Libraries |
5
0.12
10
17
1
Museums (children's) |
7.5
0.12
40
11
1
Museums/galleries |
7.5
0.06
40
9
1
Retail | |||||
Sales (except as listed below) |
7.5
0.12
15
16
2
Mall common areas |
7.5
0.06
40
9
1
Beauty and nail salons |
20
0.12
25
25
2
Sports and Entertainment | |||||
Gym/stadium (play area) |
0.3
30
2
Spectator areas |
7.5
0.06
150
8
1
Health club/aerobics room |
20
0.06
40
22
2
Gambling casinos |
7.5
0.18
120
9
1
General Notes for Table:
1. Related requirements: The rates in this table are based on all other applicable requirements of ANSI/ASHRAE Standard 62.1-2007 being met.
2. Smoking: This table applies to no-smoking areas. Rates for smoking-permitted spaces must be determined using other methods.
3. Air density: Volumetric airflow rates are based on an air density of 0.075 lbda/ft3, which corresponds to dry air at a barometric pressure of 1 atm and an air temperature of 70°F. Rates may be adjusted for actual density but such adjustment is not required for compliance with the standard.
4. Default occupant density: The default occupant density shall be used when the actual occupant density is not known.
5. Default combined outdoor air rate (per person): This rate is based on the default occupant density.
6. Unlisted occupancies: If the occupancy category for a proposed space or zone is not listed, the requirements for the listed occupancy category that is most similar in terms of occupant density, activities, and building construction shall be used.
References
ASHRAE Fundamentals Handbook, 2021
- General Ventilation Rates Table
- Heat Gain or Loss HVAC Duct ASHRAE Formula and Calculator
- Residential Duct Systems Design
- Convert Flat Oval Ducts to Round Sizes Formula and Calculator
- Duct Design Air Flow Velocities
- Accurate Heating and Cooling Load Calculations
- Ventilation Duct Stack Pressure Review, Formulas and Calculator
- Minimum Duct Insulation R-Value
- Round Duct Heat Transfer Coefficient Wall Temperature Heat Transfer Equation and Calculator
- HVAC Air Duct Flow Resistance Chart