Latent Energy Load Moisture Removal or Addition Calculator
Heat Transfer Engineering
Thermodynamics
HVAC Design and Engineering
Moisture Removal or Addition by HVAC Latent Energy Load Calculator
HVAC air exchange modifies the moisture content of air in a building. The rate of energy consumption associated with these latent loads, to add or remove water from the air and neglecting the energy associated with any condensate, is
ql = 60 · Q · ρ · ΔW ( 1061 +0.444T)
where
ql = latent heat load to remove or add moisture, Btu/h
Q = airflow rate, cfm
ρ = air density, lbm/ft3 (about 0.075 at or near sea level)
ΔW = humidity ratio difference between indoors and outdoors, lbm water/lbm dry air (lbmw/lbmda)
ΔT = average of indoors and outdoor temperature, °F
Equation (1) is known as the latent heat equation. When at or near sea level, and for common comfort air temperatures, the right hand side of Equation is approximately
ql = 4840QΔW
- General Ventilation Rates Table
- Steady-State Indoor Air Quality Formulae and Calculator
- HVAC Air Conditioning Engineering
- Accurate Heating and Cooling Load Calculations
- Air Conditioning Size Calculator and Estimator Chart This calculator is provided for use to calculate basic size in BTU to adequately cool a room of know size.
- Unit Thermal Resistances Well Sealed Air Spaces
- Overall Coefficient of Heat Transfer of a Refrigerated Space Formulas and Calculator
- Time to Freeze Piping Formulas and Calculator
- Air Conditioning System Design and Analysis Document This is an introduction to air conditioning systems (frequently referred to as HVAC systems – heating, ventilating and air conditioning systems).
- HVAC Heating Ventilation Air Conditioning
- Boiling and Freezing Point Properties of Selected Substances
- Water - Density Viscosity Specific Weight
- HVAC Air Change Out Frequency (minutes) General recommendations for total volume of air change out for selected type indoor air spaces.
- Heat Transfer Practical Approach Leidenfrost effect
Source
ASHRAE Handbook - HVAC Handbook Fundamentals, ASHRAE: 2021, page 16.12